Connect two devices to CS I/O port | CR1000 logger


koxme Aug 29, 2017 07:15 AM

Hi there

Is it possible to have two devices connected at the same time to a CSI/O port in a CR1000 logger?

In this case we want to communicate two loggers via RF416, but at the same time we need to have a MD485 module connected to the CSI/O port, is this ok?

Thanks


jtrauntvein Aug 29, 2017 12:54 PM

The configuration you describe should work fine as long as the RF416 and the MD485 are assigned different SDC address settings.  I would suggest using the network planner to generate the settings.


koxme Aug 29, 2017 01:17 PM

That´s what I though,

thanks a lot


jra Aug 29, 2017 02:00 PM

This video: https://www.campbellsci.com/videos/loggernet-software-network-planner shows how to use the Network Planner. 