I have a base and remote stations utilizing all CR1000 Loggers. I am using all RF450s.
Loggernet server has an address of 4094, Pak Bus Port = 4087 and Base Datalogger is 4020.
My two stations are PB 201 and PB 202. All have worked fine in the past. The issue is
I can connect to the base but when I try to connect to station one or two, I don't
see any activity on the Base RF450 at all. I have changed out numerous radios and the logger.
Still no joy.
Appreciate any suggestions. //repspectfully//
Wx2nite
Is the RF450 used at the base setup as the RF network master? Are the two stations RF450 setup as slaves? I would double check the Network ID and frequency keys used in the radios. Also check the receive and subnets IDs. The base radio might also need to be setup to beacon on the port the RF450 is connected to.
What changed from when it was working in the past to now? Knowing exactly what changed will point us in the direction of what the error might.