I'm seting up a station with the folowing sensors:
9 Thermocouples
4 CS500 T-RH sensores
4 Vaisala CO2 sensores (4-20mA output)
1 CS106 barometer
Since the CR1000 doesn't have enough analog channels for all the sensors I will use an AM16/32 multiplexer (I already have all the sensors, CR1000 and AM16/32).
Now I'm confused about the correct way to wire all the sensors and also the wiring between the CR1000 and the AM16/32. According to the AM16/32 manual (appendix c) a proper use of thermocouple will be to use a thermocouple wire to connect between the AM16/32 ODD H/ODD L and CR1000 H1/L1 (when datalogger reference junction is used), but in your tutorial video the presenter is using a simple wire.
Which is correct?
It is also wirtten in the manual "It is not recommended to make measurements of any other sensor type through the AM16/32B if thermocouples are measured with respect to the datalogger reference (the signal wires between the datalogger and AM16/32B are made of thermocouple wire). Two problems would arise due to the properties of thermocouple wire"
Can I use both thermocouple and other sensors with the AM16/32?
Thanks
Uri
You can use regular wire between the AM16/32 and the CR1000, if you have a temperature measurement of the AM16/32 to use as the reference for thermocouples.
Thanks JDavis.
I don't have a temperature measurement on my AM16/32.
In this tutorial the AM16/32 is wired with regular wire and in the following programing tutorial the reference temperature is the CR1000 and not a temperature measurement of the AM16/32.
What do you recommend me to do?
thanks
Uri
Any difference in temperature between the AM16/32 and the CR1000 would offset all of your thermocouple temperatures.
So I have only 2 options?
Yes
Thanks JDavis for all the answers.
Hello JDavis,
Do you know why a temperature reference is not needed using thermocouple wires betwenn the multiplexer and the controller and why we need it using regular wires?
If I keep the multiplexer and the controller(cr1000) in a enclouser, How much different could the temperature be between them? when is an AM25T worth of buying?
Thanks,
Cristian
The requirement of where the reference temperature should be measured is due to the thermoelectric effect. It it the nature of how thermocouples work. Dissimilar metals generate a differential voltage when in contact with each other. The terminals on the multiplexer and datalogger are all copper.
When you wire into the AM16/32, and back out with thermocouple wire, the voltages going in and back out cancel each other. You need a reference temperature where it stops being thermocouple wire.
There are two reasons for using a AM25T; fast channel switching time, and a good reference temperature measurement. The channel switching time is only important if you need to do your measurements fast. The AM25T has an aluminum heat spreader with a reference temperature sensor bonded to it. It ensures you don't have gradient errors across your terminals.
Compare the accuracy of the AM25T reference temperature to the panel temperature on the CR1000. The difference might not be significant for your application.
ok. Thanks JDavis!
This post is under review.