I'm wondering if there is any issue having a CR6 connected to a large 160 ah 12V AGM battery with the BAT terminals while being connected to a 24V power supply which is connected to AC power.  I don't believe the CR6 was meant to charge such a large battery, and the CR6 isn't supposed to be the main charging source, but there are times when both may be connected for long periods in my scenario and I just wanted to make sure there wasn't an issue with that.


SteveA Jan 26, 2018 05:36 PM

The 24V power supply would be connected to the CHG terminals on the CR6


JDavis Jan 26, 2018 06:59 PM

The only issue is the charger on the CR6 could take 160 hours to charge that big battery.