Packbus/TCP Clents | CR310


Anas Zaatreh Mar 28, 2018 11:50 AM

Hello,

I Have a CR310 Data-logger and i need to connect on it remotely. I surfed the device Configuration utilty and found on network services tab that i can insert server ip and the desired port, i used a static IP of the plant and used the same default port which's (6785) but still doesnt working.


jtrauntvein Mar 28, 2018 10:52 PM

Make sure you understand what the PakBus/TCP Clients sertting is doing.  This setting is instructing the datalogger that it should open and maintain connections to another process running a PakBus/TCP service.  If you are using this in LoggerNet, for instance, you would either need to set up the station in the network map so that it is either a child to a PakBus/TCP server or as a child to a regular TCP connection that has callback enabled.  If you don't do this, there will be no process available when the datalogger attempts to open the TCP connection.