The datalogger could not compile the program. line 50. Too many parameters: -1


paddysullivan May 11, 2018 01:14 AM

Hi,

I created a very simple program in ShortCut and sent it to two different CR1000s.  It seems to compile just fine in ShortCut.  I also opened it in the CRBasic editor and it compiled fine there as well.  Both dataloggers returned the error message in the subject line.  I tried creating the program in two different (recent) versions of ShortCut (on two different computers).  I also tried two different usb adaptor/cable combinations. 

See below for the program.  Any thoughts??

'CR1000

'Created by Short Cut (4.0)

 

'Declare Variables and Units

Public BattV

Public PTemp_C

Public TRHData(2)

Public PAR_Den

Public PAR_Tot

Public Rain_mm

Public WS_ms

Public WindDir

 

Alias TRHData(1)=AirTC

Alias TRHData(2)=RH

 

Units BattV=Volts

Units PTemp_C=Deg C

Units PAR_Den=umol/s/m^2

Units PAR_Tot=mmol/m^2

Units Rain_mm=mm

Units WS_ms=meters/second

Units WindDir=degrees

Units AirTC=Deg C

Units RH=%

 

'Define Data Tables

DataTable(Table1,True,-1)

                  DataInterval(0,60,Min,10)

                  Minimum(1,BattV,FP2,False,False)

                  Average(1,PTemp_C,FP2,False)

                  Average(1,AirTC,FP2,False)

                  Sample(1,RH,FP2)

                  Average(1,PAR_Den,FP2,False)

                  Totalize(1,Rain_mm,FP2,False)

                  Average(1,WS_ms,FP2,False)

                  Maximum(1,WS_ms,FP2,False,False)

                  Sample(1,WindDir,FP2)

EndTable

 

'Main Program

BeginProg

                  'Main Scan

                  Scan(30,Sec,1,0)

                                    'Default CR1000 Datalogger Battery Voltage measurement 'BattV'

                                    Battery(BattV)

                                    'Default CR1000 Datalogger Wiring Panel Temperature measurement 'PTemp_C'

                                    PanelTemp(PTemp_C,_60Hz)

                                    'CS215 Temperature & Relative Humidity Sensor measurements 'AirTC' and 'RH'

                                    SDI12Recorder(TRHData(),1,"0","M! ",1,0,-1)

                                    'LI190SB Quantum Sensor measurements 'PAR_Tot' and 'PAR_Den

                                    VoltDiff(PAR_Den,1,mV7_5,1,True,0,_60Hz,1,0)

                                    If PAR_Den<0 Then PAR_Den=0

                                    PAR_Tot=PAR_Den*8.278146

                                    PAR_Den=PAR_Den*275.9382

                                    'TE525/TE525WS Rain Gauge measurement 'Rain_mm'

                                    PulseCount(Rain_mm,1,1,2,0,0.254,0)

                                    '05103 Wind Speed & Direction Sensor measurements 'WS_ms' and 'WindDir'

                                    PulseCount(WS_ms,1,2,1,1,0.098,0)

                                    BrHalf(WindDir,1,mV2500,3,1,1,2500,True,20000,_60Hz,355,0)

                                    If WindDir>=355 Or WindDir<0 Then WindDir=0

                                    'Call Data Tables and Store Data

                                    CallTable Table1

                  NextScan

EndProg


GTProdMgr May 14, 2018 05:06 PM

The error is on this instruction:

SDI12Recorder(TRHData(),1,"0","M! ",1,0,-1)

You probably have an old OS/Firmware in the CR1000 that doesn't support the optional parameter being used.

Recommend you upgrade the OS of your CR1000 dataloggers.