Can someone suggest how to connect the Gems hall effect turbu=ine flow rate sensor FT-110
http://www.controlcomponents.com.au/products/documents/gems_flow_level/gf22_ft_110_turboflow_1.pdf
to CR6.
Is there any example code to do that using CR basic, or I can do it using the shortcut.
Thanks
The signal type is labeled as open collector. So, do a pulse measurement in switch closure mode.
If it outputs pulses in gallons, do the running average option over 60,000 ms to get gpm.