delay question


mortenx Aug 26, 2018 07:27 PM

if i am using Delay (0,60,Sec) , is the scaning still running or scanning is also delayd/stopped?

i am using 3g modem what needs 60 sec to boot and send data with httpost

line- 
SW12 (SW12_1,1 )
Delay (0,60,Sec)

 

DataTable(data1,True,-1)
	DataInterval(0,5,Min,10)
	TableFile ("CRD:data1",8,-1,500,0,Min,OutStat,LastFileName)
	Totalize(1,Rain_mm_1,FP2,False)
	Totalize(1,Rain_mm_2,FP2,False)
	Totalize(1,Rain_mm_3,FP2,False)
	Totalize(1,Rain_mm_4,FP2,False)
	Totalize(1,Rain_mm_5,FP2,False)
	Totalize(1,Rain_mm_6,FP2,False)
	
	EndTable

'Main Program 
BeginProg
    
Scan(5,Sec,40,0)
				Battery(BattV)
			PanelTemp(PTemp_C,50)
		PulseCount(Rain_mm_1,1,U1,1,0,1,0)
		PulseCount(Rain_mm_2,1,U2,1,0,1,0)
		PulseCount(Rain_mm_3,1,U3,1,0,1,0)
		PulseCount(Rain_mm_4,1,U4,1,0,1,0)
		PulseCount(Rain_mm_5,1,U9,1,0,1,0)
		PulseCount(Rain_mm_6,1,U6,1,0,1,0)
				'Call Data Tables and Store Data
		CallTable data1
		NextScan
   SlowSequence
		Scan(5,Min,1,0)
t1= data1.Rain_mm_1_Tot
t2= data1.Rain_mm_2_Tot
t3= data1.Rain_mm_3_Tot
t4= data1.Rain_mm_4_Tot
t5= data1.Rain_mm_5_Tot
t6= data1.Rain_mm_6_Tot

temp= Round (PTemp_C,1)
volt= Round (BattV,1)
  If t1>0 OR t2>0  OR t3>0  OR t4>0  OR t5>0  OR t6>0    Then
    
SW12 (SW12_1,1 )

Delay (0,60,Sec)

 HTTPPost (gurl,datag,httpresponse2,http_header2)
  
If httpresponse2="Error: failed to connect"
SW12 (SW12_1,1 )
 HTTPPost (gurl,datag,httpresponse2,http_header2)
Endif

 


JDavis Aug 27, 2018 05:04 PM

A delay in the slow sequence will not delay the main scan. The delay will wait at least 60 seconds. It may go longer, due to waiting on the main scan.