Our full technical support staff does not monitor this forum. If you need assistance from a member of our staff, please submit your question from the Ask a Question page.


Log in or register to post/reply in the forum.

Does the CR1000X contain termination and/or biasing resistors for RS-485 interface?


Italo Mar 15, 2019 11:12 AM

I need to add theses resistors when using RS485 modbus or is it built-in?


ZooKeeper Mar 15, 2019 05:27 PM

The CR1000X does not contain termination resistors on the RS485 A- and B+ terminals. We do offer the resistive ground (RG) terminal on the CR1000X that is 100 ohm resistance to ground to terminate the RS485 ground. We have found that termination resistors are rarely needed. If you need termination resistors to eliminate reflections then realize the tradeoff is that power requirements will increase.

Log in or register to post/reply in the forum.