Writing data to CR800 vie Modbus


alackey May 21, 2019 12:54 PM

Can data be written to a CR800 acting as a Modbus slave from a Micrologix 1100 Modbus Master vie RS485


JDavis May 22, 2019 05:05 PM

Yes, by default all the variables you map to registers with the ModbusSlave instruction in the datalogger are writable. 