CR6 Uninterruptible Power Supply: Solar Panel directly to CR6 or solar charge controller


fluckste May 26, 2019 10:06 AM

Hi,

I plan on deploying a CR6 with a Sonic Anemometer in the field for a month. For power Supply, I have a lead acid battery, a solar panel and a solar charge controller. Reading the manual of the cr6, I could also simply hook up the battery to the BAT terminal and the solar panel to the CHG terminal. On the other hand, I could hook up my battery and the solar panel to the solar charge controller, and that one to the BAT terminal. 
Is there a difference, will my dedicated solar charge controller be more efficient than the CR6, do I lose any functions with either method?

Kind wishes and thank you!
Stefan


smile May 27, 2019 03:40 PM

Hi,

The first step is to check the maximum current that the controller inside the logger can control.

This is related to your photovoltaic module and battery.

As for efficiency, I believe I haven't read anything in the logger's manual.

Smile


fluckste May 28, 2019 08:05 AM

Hi, thanks for your answer! 

Ok, well with my panel 50W and battery (90Ah) being quite large, I guess I'll be using the dedicated solar charge controller then.

Cheers

stefan


smile May 28, 2019 02:53 PM

Hi,

Ok I read in the manual that the internal charger in the logger can control up to 1.2A at 20°C, so it is better to use an external charger.

Smile


david056 Jun 5, 2021 10:14 AM

Whats the major difference between internal and external charges? Any priority of using these ?