Hi,
I connected a CR1000X configured with a fixed IP adress as modbus slave using Ethernet (Master = PLC).
I can access CR1000X register using CP400 software on my computer through the Ethernet network, but when I tried to connect with the PLC, the CR1000X ip adress doesn't appear like if doesn't exist on the local network.
If I used cmd "ping" on the CR1000X fix Ip adress, I have no return.
Thanks for your help.
Julien
Ping on CR1000X is disabled by default in the Network Services settings.
Perfect! Thank you very much!