Hello,
i have two loggers, a CR1000 (PakBus = 1, OS 32.03) and a CR1000X (PakBus = 2, OS 3.02). Both are connected via COM3. The CR1000X should be the master. ClockReport and PakBusClock work, SendData not.
Where is the error?
Here are the simplified programs.
Logger 1:
=============
'CR1000 Series Datalogger
Public Battery
DataTable (Station1,1,-1)
DataInterval (0,10,Min,10)
Minimum (1,Battery,FP2,False,False)
EndTable
BeginProg
SerialOpen (Com3,115200,4,0,500)
Scan (30,Sec,0,0)
Battery (Battery)
CallTable Station1
SendData (Com3,2,2,Station1,-1)
PakBusClock (2)
NextScan
EndProg
Logger 2:
=============
'CR1000X Series Datalogger
Public Battery
DataTable (Station2,1,-1)
DataInterval (0,10,Min,10)
Minimum (1,Battery,FP2,False,False)
EndTable
DataTable (Station1,1,-1)
Minimum (1,Battery,FP2,False,False)
EndTable
BeginProg
SerialOpen (ComC5,115200,4,0,500)
Scan (30,Sec,0,0)
Battery (Battery)
CallTable station2
ClockReport (ComC5,1,1)
AcceptDataRecords (1,1,Station1)
NextScan
EndProg
Best regards
(solved): Data interval and scan interval at Station1 must be identical, but I want to scan interval 30 sec. and data interval 10 min and there it does not work again.
now solved: CR1000X downgrade firmware to 3.01 and upgrade again to 3.02