Hi,
I want to connect a sensor supporting RS485 (Half duplex communication) supported sensor to CR310 datalogger. Please help me with which port to consider and what code should I refer.
Thanks,
Aishwarya
Sorry, the CR310 datalogger does not support RS485 half or full duplex connections. You would probably need to use an external RS485 to RS232 converter and then connect to the CR310 using its RS232 port or C1/C2.
Hi,
Thank you so much for the reply.As u have suggested to use the External converter I will surely consider that.For now I want to configure port c1 and c2 to communicate with my sensor supporting RS232 Communication can you please suggest how I can do so using Shortcut app.
Thanks,
Aishwarya
ShortCut does not include support for Serial sensors. You will need to use CRBasic instead.
There is a good Technical Note on this which can be found here :-
Interfacing Serial Sensors with Campbell Scientific Dataloggers (App. Note Code: 2MI-V)
If you need further support than this, then your local Campbell Scientific office will be able to help.