LorenFiedler Jul 26, 2021 08:19 PM

I am getting this warning when I send a program to the logger:

"Warning: Hardware fault: C7 bus. C7 OS. CPU:ATSG-ODI-12_TEST.CR1X -- Compiled in PipelineMode. "

I can not find any information on this error 


Nico Jul 27, 2021 04:03 AM

Does it compile in loggernet/crbasic without error?


GaryTRoberts Jul 27, 2021 03:20 PM

Loren, what is attached to C7 on the datalogger? Sometimes this error happens when there is too much votage applied to the port. C7 could also be failing if high voltage/current isn't the case.

Backing up the datalogger (with Device Configuration Utility) and then resend the latest OS (with everything removed from the datalogger's terminals, using the Send OS tab) should restore C7 operation if there isn't a hardware failure.


LorenFiedler Jul 27, 2021 03:33 PM

It turns out there was just too much current draw from the power supply so the logger was powering on and running but there were some errors, I removed a load and now everything is running smoothly 