Hi, few days ago I updated a CR310 Datalogger to current O.S versión, 10.05 version, in this update I noticed one change in the device configuration interface, this change is that the GOES tab is unavailable, is this a bug or is a definitive change?, I ask because this option is very useful for Goes Radio diagnostic. Another "bug" is in the moment to program the datalogger IP, is this case the dataloger did not take the IP, that is to say the IP is configured in option "always on" with the mask and gateway, but when the configuration is apply, not update in the report window (to the right), for example the Datalogger is configured with IP 192.168.1.10 mask 255.255.255.0 and Gateway 192.168.1.1 with ethernet power always on, the configuration is applied, but in the report window appear default network or the last IP before a new configuration, for example, if the Datalogger had 192.168.1.25, this is the IP that appear in the report window, this not allow the cominication with our server because the IP is not correct.
I was windering if you coul help me with this doubts about CR310 updates.
Thaks a lot.
Ismael Anaya.
A new option was added to the GOES configuration setting that allows you to specify the antenna gain. In order to maintain backwards compatibility, this required that a new setting be created with a different identifier and that the datalogger stop reporting the older identifier. In order to see this new setting, you will need to update your version of devconfig to 2.27.
A 2.28 version of Device Configuration Utility is being worked on with a fix for the missing GOES tab. Until then, you could load an older OS into the CR300.