Hello community,
I have a CR1000 with two sensors:
HMP45C
CS616
I used shortcut to generate the program and when using pc400 in the public table the values for CS616 are always 0.00
I have double checked the wiring diagram and I don't know why it is 0.00.
do I need to calibrate it?
how can I check it is able to work and it is not broken?
Thanks so much, any help is much appreciated.
Look at the value for the period. That is the one with the default lable of PA_uS.
The period is the raw reading before any calibration is appied.