Hi,
I'm getting mad, I need your input.
I have a CR300, and a GSM modem (ercogener 400e) piloted by the CR300. The modem is plugged on the RS232 com port, and the power is managed by the 12Vdc switch.
Using Putty, I can see my modem correctly been registred on the french network, have an IP, can ping some addresse : it's online.
Then I can see the CR300 correctly manage switch and power up the modem ; I've added a IF condition with the hour of the day, and the battery voltage.
And I configured both serial port with the correct baudrate (115200), and the modem with the correct parity (8N1).
And I configured in the PPP tab the dial string : AT+CGDCONT=1,"IP","fipbouygtel.com";ATD*99***1#
When I plug the 400e and the CR300, I'm connecting with DevConfig Utility to looking on the PPP page to see the communication between the two devices, and it never pass the stages :
ppp state: dialing START -> dialing ECHO
ppp state: dial failed -> dialing START
ppp state: dialing OFFLINE -> dialing ECHO_ATH
Then turn in loop.
Here is my prog (I've hide my credentials of dydns off course) :
'CR300/CR310 'Created by Short Cut (4.4) 'Declare Variables and Units Public BattV Public PTemp_C Public TRHData(2) Public WS_ms Public WindDir Public T107_C_010 Public T107_C_150 Public T107_C_300 Public SlrW Public SlrkJ Public Rain_mm Public TimeOffset="NAN" Alias TRHData(1)=AirTC Alias TRHData(2)=RH Units BattV=Volts Units PTemp_C=Deg C Units WS_ms=meters/second Units WindDir=degrees Units T107_C_010=Deg C Units T107_C_150=Deg C Units T107_C_300=Deg C Units SlrW=W/m^2 Units SlrkJ=kJ/m^2 Units Rain_mm=mm Units AirTC=Deg C Units RH=% Dim rTime(9) Alias rTime(1)= Time_Year Alias rTime(2)= Time_Month Alias rTime(3)= Time_DayOfMonth Alias rTime(4)= Time_HourOfDay Alias rTime(5)= Time_Minutes Alias rTime(6)= Time_Seconds Alias rTime(7)= Time_Microseconds Alias rTime(8)= Time_DayOfWeek Alias rTime(9)= Time_DayOfYear '----------MODEM parametres Const GPRS_ModemBaudRate = 115200 Const GPRS_ModemPort = ComRS232 Const GPRS_CR = CHR(13) Const GPRS_OK = CHR(10)& "OK" Public ppp As String * 50 Dim pppOld As String * 50 Public TelecomFlag As Boolean 'True if telecom powered Public TelecomStartTime = 7 'UTC Public TelecomStopTime = 20 'UTC '----------MODEM parametres '----------DynDNS parametres Dim Socket Dim SocketResponse As String * 200 Dim pppInfo(9) As String *32 Dim UDDNScont = 0 Const dyndnshostname="XOXOXOXOXOXOXOXOXO" Const dyndnsauth="XOXOXOXOXOXOXOXOXO" 'Const SocketGetRequest="GET /nic/update?hostname="+dyndnshostname+"&myip=ipaddress&wildcard=NOCHG&mx=NOCHG&backmx=NOCHG HTTP/1.0"+CHR(13)+CHR(10) Const SocketGetRequest="GET /nic/update?hostname="+dyndnshostname+"&myip=ipaddress HTTP/1.0"+CHR(13)+CHR(10) '----------DynDNS parametres 'Define Data Tables DataTable(meteo,True,-1) DataInterval(0,10,Min,10) Average(1,T107_C_010,FP2,False) Average(1,T107_C_150,FP2,False) Average(1,T107_C_300,FP2,False) Average(1,AirTC,FP2,False) Sample(1,RH,FP2) WindVector(1,WS_ms,WindDir,FP2,False,0,0,0) FieldNames("WS_ms_S_WVT,WindDir_D1_WVT,WindDir_SD1_WVT") Average(1,SlrW,FP2,False) Totalize(1,SlrkJ,IEEE4,False) Totalize(1,Rain_mm,FP2,False) EndTable DataTable(soh,True,-1) DataInterval(0,60,Min,10) Minimum(1,BattV,FP2,False,False) Minimum(1,PTemp_C,FP2,False,True) EndTable '---------MODEM sous-routine Sub ModemON 'procedure de démarrage du modem PortSet (SW12V,1) TelecomFlag = True Delay(1,45,sec) ppp=IPInfo (1,0) If ppp="" OR ppp="0.0.0.0" Then ppp=PPPOpen EndIf Delay(1,20,sec) EndSub Sub ModemOFF 'arret du modem PPPClose SerialOpen(GPRS_ModemPort,GPRS_ModemBaudRate,0,20000,100) SerialOut(GPRS_ModemPort,"AT+CFUN=0" & GPRS_CR,GPRS_OK,3,200) Delay(1,5,sec) SerialOut(GPRS_ModemPort,"AT+CPWROFF" & GPRS_CR,GPRS_OK,3,200) Delay(1,30,sec) 'delay a few more seconds just to be sure the modem is off SerialClose(GPRS_ModemPort) 'Release the serial port connection. PortSet (SW12V,0) 'Turn off the modem (when necessary) pppOld="0.0.0.0" EndSub Sub UpdateDDNS Socket=TCPOpen("members.dyndns.org",80,8245) If Socket<>0 Then SerialOut(Socket,SocketGetRequest,"",0,0) SerialOut(Socket,"Host: members.dyndns.org "+CHR(13)+CHR(10),"",0,0) SerialOut(Socket,"Authorization: Basic "+dyndnsauth+CHR(13)+CHR(10),"",0,0) SerialOut(Socket,"User-Agent: Company - Device - Version Number"+CHR(13)+CHR(10),"",0,0) SerialOut(Socket,CHR(13)+CHR(10),"",0,0) SerialIn(SocketResponse,Socket,1000,"",200) SplitStr (pppInfo,SocketResponse,CHR(13)+CHR(10),9,5) UDDNScont = UDDNScont+1 EndIf EndSub'---------MODEM sous-routine 'Main Program BeginProg TelecomFlag = False 'Main Scan Scan(30,Sec,1,0) 'Default CR300 Datalogger Battery Voltage measurement 'BattV' Battery(BattV) 'Default CR300 Datalogger Processor Temperature measurement 'PTemp_C' PanelTemp(PTemp_C,50) 'CS215 Temperature & Relative Humidity Sensor measurements 'AirTC' and 'RH' SDI12Recorder(TRHData(),C1,"0","M!",1,0,-1) '03002 Wind Speed & Direction Sensor (CSL) measurements 'WS_ms' and 'WindDir' PulseCount(WS_ms,1,P_LL,1,1,0.75,0.2) If WS_ms<0.21 Then WS_ms=0 BrHalf(WindDir,1,mV2500,1,VX1,1,2500,False,20000,50,352,0) If WindDir>=352 Or WindDir<0 Then WindDir=0 '107 Temperature Probe (CSL) measurement 'T107_C_010' Therm107(T107_C_010,1,2,VX1,0,50,1,0) '107 Temperature Probe (CSL) measurement 'T107_C_150' Therm107(T107_C_150,1,3,VX1,0,50,1,0) '107 Temperature Probe (CSL) measurement 'T107_C_300' Therm107(T107_C_300,1,4,VX1,0,50,1,0) 'CMP3/CMP6/CMP11 Pyranometer (CSL) measurements 'SlrkJ' and 'SlrW' VoltDiff(SlrW,1,mV2500,3,True,0,50,1,0) If SlrW<0 Then SlrW=0 'Calculate total flux 'The multiplier to calculate total flux was calculated by Short Cut 'and based on a program execution rate (scan rate) of 30 Seconds. 'If you change the program execution rate outside of Short Cut with the CRBasic Editor 'you will need to recalculate this multiplier. See the sensor manual for more details. SlrkJ=SlrW*1 'Calculate flux density SlrW=SlrW*33.33333 'Generic Tipping Bucket Rain Gauge measurement 'Rain_mm' PulseCount(Rain_mm,1,P_SW,2,0,0.2,0) 'Call Data Tables and Store Data CallTable meteo CallTable soh NextScan '---------MODEM slowsequence SlowSequence Scan(1, Min, 3, 0) If BattV >=11.25 Then RealTime (rTime) 'get various time elements If Time_HourOfDay >= TelecomStartTime AND Time_HourOfDay <= TelecomStopTime Then ' activate telecommunication If TelecomFlag = False Then ModemON EndIf ppp=IPInfo (1,0) If ppp <> pppOld OR ppp = "0.0.0.0" Then UpdateDDNS pppOld = IPInfo (1,0) TimeOffset = NetworkTimeProtocol ("145.238.203.14",0,1000) EndIf Else If TelecomFlag = True TelecomFlag = False ModemOFF EndIf EndIf Else If TelecomFlag = True TelecomFlag = False ModemOFF EndIf EndIf Next Scan EndSequence '---------MODEM slowsequence EndProg
Hey,
is there anybody that could have an idea about this ?
I'm still stuck with this CR300 / modem communication...
Hey again,
it was a hardware problem ; The ercogener manufacturer DB-9 to DB-15 cable was wrongly wired...
Hard to guess. I made a cable myself : it works immediatly.
Everything works fine now.