Hi. I have several CRVW3-RF451 (all slaves) and a RF451 (master) they all working fine. Now I need to add to the network a CR10X-PB connected by SC932A to another RF451(slave), but Im trying and Loggernet can´t see this.
I try with NetworkPlanner but nothing. I consider all pakbus ok and same ID network. CR10X-PB is running ok alone
What am I doing wrong? Is there any special instruction in the CR10X program? ( the program have P190 and P191 instructions)
An RF451 would connect to a CR10X-PB directly via CS I/O. There is not a need for a SC932A.
If you want to use Network Planner, you drop a CR10X-PB onto the model canvas and then drop a RF451/RF452 directly onto the CR10X-PB. Network Planner will show a configuration of the CR10X-PB and RF451 connected via CS I/O with SDC address 7.
No special instruction is needed.
OK. Now is working fine.