Hi Campbell,
We have a project that required to log 2 VW sensors in 1 sec each take. (2 VW channels per second)
Can CR6 log CDM VW300 with that speed?
or is there any other alternative way to do this?
Thanks & Best Regards
Jimmy.c.c
The CR6 can measure 1 VW sensor per second (directly with no peripheral devices). So to measure 2 VW sensors would take it 2 seconds. So you are correct that you will need a CDM-VW300 or CDM-VW305 to get both sensors at a once-per-second measurement rate. The CDM does connect to the CR6 directly using a CPI cable. Take a look at the CDM-VW300 manual for details.
https://s.campbellsci.com/documents/us/manuals/cdm-vw300.pdf