Using ExciteV with a CR6 universal channel


Erik_NRCan Apr 7, 2017 07:29 PM

Has anyone used a universal channel as a continous analog output? I've used output channel successfully with a CR3000 in the past but I'm not having much luck implmenting it with a CR6. The channel outputs the deseried voltage for a fraction of a second then goes to zero. I'm running a 1 second scan rate and I've tired a bunch of different delay values, includint zero. Also the example code in CRBasic Help does not turn the channel on (the delay is set to 200 microseconds). 


JDavis Apr 7, 2017 07:31 PM

If you use a delay of 0, the excitation channel is kept on only until all analog instructions within that scan are completed. There is not a continuous analog output function on the CR6 like the CAO port on the CR3000.


Erik_NRCan Apr 7, 2017 07:33 PM

Thank you for your reply. Is there a way to program one of the CR6 universal channels to behave as a continous analog output?


JDavis Apr 7, 2017 07:51 PM

The CR6 does not have any continuous analog output circuitry. You would have to use an external module such as the SDM-AO4A


Erik_NRCan Apr 7, 2017 08:14 PM

The SDM-A04A looks like it would work well for my application. I'm already using op-amps with the output so I'm going to try setting them up to do "sample and hold" using mosfets and capacitors.


Nigel Apr 10, 2017 12:52 AM

I set the port high pre the scan, seems to work

 

BeginProg

     ' pressure sensors, 5V from
     PortSet(U8,1)' Excite 5v U8 for the Pressure sensor

     Scan (1,Sec,0,0)

          'Psensor Pmv reading
          VoltSe(Pmv,1,mV5000,U10,1,0,50,Pmulti,Poffset)
    NextScan

 


JDavis Apr 10, 2017 03:41 PM

A Portset() will persist. However, it is not outputting a tightly regulated voltage.

If your sensor requires an excitation voltage, you should be using a bridge measurement instruction like BrHalf().


Erik_NRCan Apr 11, 2017 01:46 PM

We use dataloggers for sensing and control. If it is possible to change firmware to allow the U* terminals to be deployed as continous analog voltage outputs this would greatly expand the versitilty of the CR6.


JDavis Apr 11, 2017 02:33 PM

It is not a matter of firmware. The hardware does not exist in the CR6 for continuous analog output. That functionality can be added by connecting a SDM-AO4A or SDM-CVO4.