Is possible my CR310 like slave can get communication modbus WiFi with a PLC siemmens S7-300?
what I need It plus?
As far as i know, its possible, the datalogger can act as a modbus slave in the network.
There is some instructions in CRBasic to configure the datalogger as Slave or Master in a Modbus network,
You can see help in CRBasic over this instructions:
ModbusSlave
ModbusMaster
The datalogger dont have a modbus map, but you can create registers in the program and asign a modbus addres to each variable then you have to configure this addres in the PLC "modbus master" to poll the information from the datalogger.
You can see also:
https://s.campbellsci.com/documents/us/technical-papers/dataloggers-as-modbus-slave-devices.pdf